Default Insulating slab with Super Isol

I have purchased the Super Isol board from James... (Thanks James! Your help is appreciated!)
My question is what thickness should I make my insulating hearth now so it is strong enough to support my oven. 2"...4" Do I still need to do 6"?

Thanks
Mike
Reply With Quote
  #2  
Old 08-01-2006, 10:40 AM
dmun's Avatar
Moderator
 
Join Date: Jul 2005
Location: New Jersey USA
Posts: 4,216
Default thickness of support slab

4" of reinforced concrete is what is called for: This gives you two inches on either side of the grid of re-bar. Remember to keep the ends of the re-bar away from the edge of the slab, but long enough to be above the source of support.
Reply With Quote
  #3  
Old 08-01-2006, 12:19 PM
Peasant
 
Join Date: May 2005
Location: Hershey, PA
Posts: 48
Default

Are you using one layer or two if the Super Isol?

Last edited by Alan; 08-01-2006 at 12:36 PM.
Reply With Quote
  #4  
Old 08-01-2006, 01:19 PM
Laborer
 
Join Date: Apr 2006
Location: Upland, Ca
Posts: 76
Default

I just purchased it...I only bought enough for 1 layer.


Should the rebar be lon enogh to reach the blocks end to end? Or does that matter?

Thx
Mike
Reply With Quote
  #5  
Old 08-01-2006, 01:24 PM
james's Avatar
Brick Oven Merchant
 
Join Date: Mar 2005
Location: Pebble Beach, CA
Posts: 4,648
Default

Thermally, one layer does it. 4" of vermiculite concrete has proven to be enough to effectively block heat movement, and the 2" Super Isol should do a better job than that. I think we're in a safe zone.

For the rebar, your lengths should reach to the top of block stand, but not go to the end. You want concrete "around" the rebar, with the rebar "resting" in the center of the slab, on the blocks.

From our concrete experts, structurally -- why is that true?

James
__________________

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Last edited by james; 08-01-2006 at 01:27 PM.
Reply With Quote
  #6  
Old 08-01-2006, 03:49 PM
Alf's Avatar
Alf Alf is offline
Laborer
 
Join Date: Mar 2005
Location: Cumbria UK
Posts: 58
Default

Reinforcing steel should be encased in a minimum of 50 mm (2") of concrete to protect the steel from the elements and thus rusting. Thatís according to our Uk building regulations and the fact we live on a generally wet / damp Island.

Alf
Reply With Quote
  #7  
Old 08-01-2006, 07:46 PM
Peasant
 
Join Date: May 2005
Location: Hershey, PA
Posts: 48
Default

Rebar can be placed in different locations in the slab according to the size of the slab and the loading. It will generally keep the parts of the slab from separating if it cracks, and can make it stronger as well. A slab that's resting on its edges and loaded at the center will be in tension on the bottom and in compression on the top (think of the slab sagging a very tiny amount with the top concave and the bottom convex - this is how the slab will move, though the movement will certainly be too tiny to see).

Concrete is much weaker in tension than in compression, so if the slab were heavily loaded you'd put the rebar near the bottom where it's in tension but be sure, as Alf says, to have enough concrete to protect it from corrosion. I imagine that a 4" slab is very lightly loaded compared with its ultimate strength, which is why people do fine putting the rebar near the center. It still adds integrity and strength to the slab. If it were to begin to crack, the sections are held together and can't go anywhere.
Reply With Quote
  #8  
Old 08-01-2006, 09:21 PM
Laborer
 
Join Date: Apr 2006
Location: Upland, Ca
Posts: 76
Default adding a center section

I know its not necessary but I am leaning toward adding a center section of blocks to support the middle of the slab. I also plan on usig concrete backer board instead of plywood and just leave it there.
So I will pour the slab on top of the backer board and then put the super isol on top of the slab..then the oven on top of that.
Reply With Quote
  #9  
Old 08-02-2006, 05:38 AM
dmun's Avatar
Moderator
 
Join Date: Jul 2005
Location: New Jersey USA
Posts: 4,216
Default

A reminder; if you block in the back section completely, you need to put in a vent. If the point is just additional support, you could just add a stack of blocks on each side, and still have the additional wood storage. Remember: the oven distributes most of it's weight to it's edges. Just building a pier in the center wouldn't be that useful.

Other than that, your plan sounds good.
Reply With Quote
  #10  
Old 08-02-2006, 06:16 AM
Serf
 
Join Date: Jun 2006
Location: bay area
Posts: 16
Default layer of super isol and 2" of vermiculite

I wanted to put 4" of concrete super isol and 2" of vermiculite in that order. That will put my top of landing at 42.5". Two questions. 1. Is that to high? and 2. Can I pour the concrete slab, Put super isol on top with no adhesive and then pour the vermiculite over? I wanted to do this so I would not have to adhere super isol to vermiculite layer. Please let me know your thoughts thank you.
Carlo
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -7. The time now is 04:18 AM.

Powered by vBulletin® Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.6.0
© 2006/10 Forno Bravo, LLC